Re: Pool Equipment room bonding
For all electrical equipment associated with the recirculating system of the specified body of water, any pump motors, underwater luminaires, and panels and their feeders, that supply pool equipment, the equipment grounding conductor run with the supply conductors is sufficient for grounding purposes, provided that the EGCs are connected to non-current carrying metal parts of the equipment; RMC, IMC, RNC, and listed MC cable are the wiring methods (EMT on and in and ENT in buildings); and the EGC is insulated copper minimum #12. See 680.6,.21(A)(1),.23(F) &.25(B)
Bonding is done for all metal equipment in and around the pool up to 12 feet above and five feet around. Also, all pump motors, pool cover motors, heaters, purifiers, etc. shall be tied into the bonding grid. 680.26.
Bring the #8 solid copper bonding conductor to any pumps, but it is not necessary to bring it to the receptacle. The purpose is to create a common voltage potential around the pool. The grid is extended to the circulating system to eliminate any currents from flowing in the piping water.