Hello everyone. My field of expertise is residential troubleshooting. I have experience with pools, but not lots of experience.
I always see pool pump motors protected by 20 amp double pole circuit breaker. Even on pool pump motors that are 9 amps on each leg.
It is my understanding for the starting current you need to rate the circuit breaker at max 150% of the load.
9(amps) x 150% = 13 amps.
Since the lowest breaker available is a 15 amp, this means that a 15 amp would be just fine, right?