Hendrix
- New England
where does it say in 680 that grounding electrode cannot be broken?
I should have said "spliced".I don't think it does. However, the requirements for grounding electrodes are pretty straightforward and a broken one (whatever you mean by broken) might well not meet the requirements.
Why would a pool have a grounding electrode conductor?
That was what I was thinking. I figured he meant equipotential bonding.Why would a pool have a grounding electrode conductor?
Sorry for the confusion. What I think I meant is..... the equipment ground from the panel, has to be insulated, therefore in conduit, out to the pool panel. Does the insulated equipment ground also have to be "without a splice" or, in other words "unbroken" to the pool equipment?
300.13
Thanks, Dennis. I may have dreamt it :roll:There is nothing in 680.25 that states the equipment grounding conductor must be unspliced
you may have been thinking of the equipment ground for pool lighting