Thank you. I meet with the pool installer on Monday. I don't even know enough to ask questions about this. I barely opened the box. He has a lot of conduits run into the pool house for heaters, pool covers, etc. Most conduits are empty yet. He has said, the customer will be able to operate some of these from his phone. I don't know anything about these relays. I appreciate your help.
There will be up to 10 2-pole relays inside of the Intellicenter.
Variable speed pumps do not require use of a relay; they have a 4-wire control cable that lands on a terminal strip with a phoenix connector behind the top control panel. If they have a heat pump, you will need to provide an additional 4 conductors for integration into the Intellicenter, along with the power circuit.
If they’re using a gas heater, there is a 2-wire dry-contact terminal on the back of the control panel that you will loop the fireman’s switch inside the gas heater through to switch it off/on.
The VS pumps although not connected to a relay will still utilize a relay channel; so if you had a single VS pump and a booster pump, Channel 1 is dedicated to the VS pump, so you need to connect the booster pump relay to channel 2.
You can utilize the solar heat channels to control a relay if needed. So that would be useful if you had multiple VS pumps taking away from your control channel count but needed that relay to control additional equipment. Every button on that panel can be programmed and labeled in the app to control anything.
The lighting, blower, etc, need to connect to a relay.
The pool cover will probably be a hydraulic pump with a key switch or keypad; that control switch must be installed within sight of the pool. You need 1 circuit for the pump, and 1 circuit for the key switch. The pump voltage will depend on size; some are 120v, some 240v. The switch will likely be 120v, and it does not connect to a relay.
There is a salt chlorinator transformer inside the panel that needs to be routed through a relay as well so they can program it to lock out when the filter pump isn’t running. You’ll also have a board control transformer that can be powered by 120v or 240v. I power both transformers from the same breaker.
As for programming, the pool builder should be handling that; they can setup a program remotely and load it via a USB stick. The new Intellicenter panels can connect via WiFi. Previously you needed either an Ethernet connection or a wireless bridge connected to Ethernet inside the house.
Also, you need to extend the shell bonding wire to the Intellicenter because of the salt chlorinator transformer being installed inside. There are two lugs on the bottom right hand corner for this.
There will be some temp sensors and valve actuator control wires that need to go through the LV compartment on the left side of the panel. One is air temp, and you will have another for water temp.
If you have VS pumps, make sure you torque those lugs properly because they are susceptible to failure if not done correctly; i use crimp fork connectors on those as well. For single speed pumps I use a right-angle crimp spade connector.