pierre
- Westchester County, New York
Re: Pool pump circuit- why in conduit?
Section 680.21 Takes a little extra reading to fully (if that is possible) understand it.
In dwellings, the wiring methods for branch circuits 'INSIDE' the building [680.21(A)(4)] can be a 'Chapter 3' method. Once the wiring 'leaves' the building, the installer has to follow 680.21(A)(1). This only permits a raceway type method or MC type cable listed for the location. So you cannot use UF cable to feed it outside.
Why do they only permit these types of wiring methods in my 'guess' would be their concern about Chlorine and the Protection of the EGC. If one was to locate the year this decision was made, then you could read in the ROP or ROC the substantiation of the decision.
Pierre
Pierre