I'm wiring a new pool at a single family residence. I'm planning on adding a subpanel near the equipment which will be on the side of the house exposed to the weather.
1. The pump is a 230V 1.5 HP, Variable Speed, .4 - 5.6 Amps
Breaker - I figured it to be - 1.5 HP = 10 x 2.50 = 25 Amps (430.248, 430.52)
Conductors - 1.5 HP = 10 x 1.25 =12.5 Amps 15 Amps - 14 AWG (430.248, 430.22A)
The owner wants to cord and plug connect the pump. How can I do this? I don't believe there is a 25 Amp, 240V receptacle. Would I be better off just hard-wiring it, since the panel will be only 10' away?
2. Since the subpanel will be mounted outside the residence and not in a separate structure, I won't need to drive a ground rod, correct?
3. The pool is located 4' 6" from the side of the house which has aluminum siding. I believe I have to bond this, is it as simple as installing a lug and hitting it with a #8 to the pool bond?
Thanks,
1. The pump is a 230V 1.5 HP, Variable Speed, .4 - 5.6 Amps
Breaker - I figured it to be - 1.5 HP = 10 x 2.50 = 25 Amps (430.248, 430.52)
Conductors - 1.5 HP = 10 x 1.25 =12.5 Amps 15 Amps - 14 AWG (430.248, 430.22A)
The owner wants to cord and plug connect the pump. How can I do this? I don't believe there is a 25 Amp, 240V receptacle. Would I be better off just hard-wiring it, since the panel will be only 10' away?
2. Since the subpanel will be mounted outside the residence and not in a separate structure, I won't need to drive a ground rod, correct?
3. The pool is located 4' 6" from the side of the house which has aluminum siding. I believe I have to bond this, is it as simple as installing a lug and hitting it with a #8 to the pool bond?
Thanks,