I am running the electrical for a pool scoreboard at a school. The plans show 4 dedicated circuits mounted on the back of the scoreboard (located about 12' from the pool edge and 15' minimum from the pool deck). The scoreboard company wants those 4 dedicated circuits to be duplex receptacles but not GFCI protected and mounted in 4 different spots on the back of the scoreboard framing.. This is an outdoor pool and I don't want to install non GFCI receptacles outdoor even if they are between 15' and 20' above the pool deck.. Apparently each circuit has 4 different PSU's that leak a total of about 3 ma per circuit. When the scoreboards get a little older they trip if on GFCI's.
My solution is to install 4 junction boxes(instead of receptacles) so I don't have to have GFCI protection. I would then need to install switches (disconnects) for each circuit at the scoreboard as I see this as a sign (article 600) and I would now need a disconnecting means. Since this is not pool circulation related equipment I don't think the sign would need GFCI if it was hardwired and had disconnects. Does this sound like it would be code compliant? Am I missing something. The scoreboard company is fine with hard wiring if it means I don't need GFCI protection.
My solution is to install 4 junction boxes(instead of receptacles) so I don't have to have GFCI protection. I would then need to install switches (disconnects) for each circuit at the scoreboard as I see this as a sign (article 600) and I would now need a disconnecting means. Since this is not pool circulation related equipment I don't think the sign would need GFCI if it was hardwired and had disconnects. Does this sound like it would be code compliant? Am I missing something. The scoreboard company is fine with hard wiring if it means I don't need GFCI protection.