I think I would just swap out the NM for some MC and be done with it. :smile:
680.23(F) gives you a list of wiring methods you can use for branch circuit wiring for underwater luminaires, NM cable is not one of them.
Chris
Chris, if the pool lights terminate in the panel then a switch leg to control the lights can be of any wiring method. IMO of course.
I don't see how per the wording posted.
No matter how you do it the switch leg is part of the supply side branch circuit wiring.
I don't see how per the wording posted.
No matter how you do it the switch leg is part of the supply side branch circuit wiring.
I still dont see how MC would be legal either?
and where installed within buildings, electrical nonmetallic tubing, Type MC cable, electrical metallic tubing, or Type AC cable shall be permitted. In all cases, an insulated equipment grounding conductor sized in accordance with Table 250.122 but not less than 12 AWG shall be required.
I think I would just swap out the NM for some MC and be done with it. :smile:
F) Branch-Circuit Wiring.
(1) Wiring Methods. Branch-circuit wiring on the supply side of enclosures and junction boxes connected to conduits run to wet-niche and no-niche luminaires, and the field wiring compartments of dry-niche luminaires, shall be installed using rigid metal conduit, intermediate metal conduit, liquidtight flexible nonmetallic conduit, rigid polyvinyl chloride conduit, or reinforced thermosetting resin conduit. Where installed on buildings, electrical metallic tubing shall be permitted, and where installed within buildings, electrical nonmetallic tubing, Type MC cable, electrical metallic tubing, or Type AC cable shall be permitted. In all cases, an insulated equipment grounding conductor sized in accordance with Table 250.122 but not less than 12 AWG shall be required.
They tell us so. :smile:
In my opinion the 'and' means all methods listed could be used inside.
In my opinion the 'and' means all methods listed could be used inside.
The "and" is in reference to on the building not the other methods. The "AND" has no relationship to the other methods.
Bob I am just trying to point out that this article may need some work. We all know what it should say but I don't think it says it.
Bob I am just trying to point out that this article may need some work.
No matter how you do it the switch leg is part of the supply side branch circuit wiring.
Yes the switch leg. From the pool panel, to the switch located in the interior of the house I have a 12-2 romex. Just to turn the pool light on and off.
That is code compliant. I've been wireing it that way for 36 years and inspecting it for 3.
I do not know if I would publically say this...That is code compliant. I've been wireing it that way for 36 years and inspecting it for 3.