I am caught between my electrician and the building official. Can someone help me out on this.
Let me start with.
*I have 3/4" ENT running along a wall. It will be very hard to attempt to sister up another conduit run next to it.
*In the 3/4" ENT I have 1 220v 20A circuit (2 Hot [both black], 1 Ground [green]) and I have a 120v 20A circuit (1 Hot [red], 1 Common [white], [Shares the same ground]. All are 12 AWG solid copper. So total of 5 conductors.
*The 3/4" ENT Terminates to a water tight pull box. This large box feeds two 120v lights tied to the 120v 20A circuit. The 220v 20A circuit feeds the pump, heater, and Salt Generator. So one 3/4" in and 5 1/2" conduits out.
*My electrician got into it with the inspector of a small town. I have to prove to the inspector that my electrician is correct, or I am going to have to run another conduit and I have no idea where I can run it with our killing my margin.
Does this sound ok, or what do I need to look deeper into?
I believe that I am OK with 5 conductors in a 3/4" ENT. Max is 6 at #12.
How can I tell what the pull box is rated for in respect to the number of ties or feeders.
Is it ok to share the ground between two feeder circuits? Does it need to be larger then 12 AWG? Is it as simple as 2 20A circuits = 40A and the ground should be rated for 40A [#10 Ground]?
My electrician is helping me out, but I want to confirm what I am hearing before I call the city back.
Thanks in advance.
CT
Let me start with.
*I have 3/4" ENT running along a wall. It will be very hard to attempt to sister up another conduit run next to it.
*In the 3/4" ENT I have 1 220v 20A circuit (2 Hot [both black], 1 Ground [green]) and I have a 120v 20A circuit (1 Hot [red], 1 Common [white], [Shares the same ground]. All are 12 AWG solid copper. So total of 5 conductors.
*The 3/4" ENT Terminates to a water tight pull box. This large box feeds two 120v lights tied to the 120v 20A circuit. The 220v 20A circuit feeds the pump, heater, and Salt Generator. So one 3/4" in and 5 1/2" conduits out.
*My electrician got into it with the inspector of a small town. I have to prove to the inspector that my electrician is correct, or I am going to have to run another conduit and I have no idea where I can run it with our killing my margin.
Does this sound ok, or what do I need to look deeper into?
I believe that I am OK with 5 conductors in a 3/4" ENT. Max is 6 at #12.
How can I tell what the pull box is rated for in respect to the number of ties or feeders.
Is it ok to share the ground between two feeder circuits? Does it need to be larger then 12 AWG? Is it as simple as 2 20A circuits = 40A and the ground should be rated for 40A [#10 Ground]?
My electrician is helping me out, but I want to confirm what I am hearing before I call the city back.
Thanks in advance.
CT