Does a hardwired 220 volt 20 amp circuit that supplies an inground swimming pool motor need to be GFI protected?
sparkyjpb said:Does a hardwired 220 volt 20 amp circuit that supplies an inground swimming pool motor need to be GFI protected?
stickboy1375 said:No, but I believe that changed in the 2008.
overmyhead said:so are we talking all 15 and 20 amp single pole and two pole?
NEC 2008 said:680.22(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.