Re: Poor design choice
The same one that requires two in the kitchen.Originally posted by infinity:
Bob, what article are you saying requires 2 SA's in the dining room?
210.52(B) (1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets covered by 210.52(A) and (C) and receptacle outlets for refrigeration equipment.