On pole mounted transformers, the state of California considers any ground within reach of a lineman a signifigant hazard. Cases of tranformers, guy wires, etc. are required to be isolated from ground to reduce the possibility of incidental contact. All transformers used in California (as far as I know) are two bushing transformers. Some utilities allow "common neutrals" where the primary and secondary neutrals are tied together and grounded and some do not. This applies to overhead only.
When a separate neutral is used, the primary neutral is considered a phase.
Getting a little off the original post, but a good topic anyway.
Everywhere I have been they not only ground transformer case, but they ground guy wires, and almost every thing else non current carrying that is conductive. That way all the non current carrying items are at same potential and you know that the ungrounded conductors is all you can't touch without proper equipment. I can't recall seeing any hot work being done in recent years by a guy on the pole - they are always in bucket truck if handling anything live and have gloves, blankets, and anything else you can think of to help isolate things.