At another plant like mine, they have a new recurring issue each evening between that lasts up to 20 minutes, and always 10 pm and 11 pm.
The background is that there are normally two directions by which the POCO supplies their plant @ 12600V. One had a problem and was taken out of service for repairs. The POCO was contacted about a possible problem on their side and POCO put a recorder on their primary side for one day and said there was no problem. The plant feels there are loads being brought onto the grid nearby that are causing this problem (there is a nuke plant 5 miles away...).
My co-worker's plant owns transformers to use 480V 3-phase. Every single evening since the one supply was taken out of service, the utility power causes the plant's switchgear to trip out on device 47, a phase protective relay, and start our emergency generator. This relay watches for phase unbalance, phase loss, and phase reversal on the incoming power, and based on his waveforms from last week, the phase unbalance is tripping.
Now, they have PF capacitors, and the tech at that plant said you can hear the power changing and can tell when it is occurring as they really go crazy when the event occurs. The plant electrician captured the same ugly waveforms on the utility power last night but this time, he was running on generator and the utility was not in service at the time.
I'm taking my Power Quality Analyzer over there on Monday to capture the waveforms and check for harmonics, so he can show them to the POCO, and maybe they will do something because they are not sure when the other feed line will be back in service.
One question I have is : if harmonics on the utility are the problem, will they still show up if the plant is not using the utility power as I capture the data (will be running on generator)?
kent
The background is that there are normally two directions by which the POCO supplies their plant @ 12600V. One had a problem and was taken out of service for repairs. The POCO was contacted about a possible problem on their side and POCO put a recorder on their primary side for one day and said there was no problem. The plant feels there are loads being brought onto the grid nearby that are causing this problem (there is a nuke plant 5 miles away...).
My co-worker's plant owns transformers to use 480V 3-phase. Every single evening since the one supply was taken out of service, the utility power causes the plant's switchgear to trip out on device 47, a phase protective relay, and start our emergency generator. This relay watches for phase unbalance, phase loss, and phase reversal on the incoming power, and based on his waveforms from last week, the phase unbalance is tripping.
Now, they have PF capacitors, and the tech at that plant said you can hear the power changing and can tell when it is occurring as they really go crazy when the event occurs. The plant electrician captured the same ugly waveforms on the utility power last night but this time, he was running on generator and the utility was not in service at the time.
I'm taking my Power Quality Analyzer over there on Monday to capture the waveforms and check for harmonics, so he can show them to the POCO, and maybe they will do something because they are not sure when the other feed line will be back in service.
One question I have is : if harmonics on the utility are the problem, will they still show up if the plant is not using the utility power as I capture the data (will be running on generator)?