Interesting, it looks like the product is at end of life and now is supported by PowerWare. See http://www.powerware.com/Products/end_of_life_Manuals.asp?CX=3 I haven't totally digested the manual but it looks like the product is normally in the rectifier/battery/inverter path except when in static bypass.
Think of the UPS system as like a canary in a coal mine, it may provide a lot of clues when facing a PQ issue.
What KVA rating are they, that would help locate the official specifications on PowerWare's web site? The specs you linked to say [FONT=Verdana, Arial, Helvetica, sans-serif]"Input 5% or less; output maximum 3% linear load" but that's on a reseller's site. [/FONT]Can't understand the claim there is no rectifier, how would they charge the batteries?
[FONT=Verdana, Arial, Helvetica, sans-serif]
I'm guessing the UPS could be 8 years old. So the questions are:
[/FONT]
Think of the UPS system as like a canary in a coal mine, it may provide a lot of clues when facing a PQ issue.
What KVA rating are they, that would help locate the official specifications on PowerWare's web site? The specs you linked to say [FONT=Verdana, Arial, Helvetica, sans-serif]"Input 5% or less; output maximum 3% linear load" but that's on a reseller's site. [/FONT]Can't understand the claim there is no rectifier, how would they charge the batteries?
[FONT=Verdana, Arial, Helvetica, sans-serif]
I'm guessing the UPS could be 8 years old. So the questions are:
[/FONT]
- How well are they maintained and how old are the batteries?
- Did they go on battery when the events occur?
- Did they drop load or go to staic bypass (that could happen if the batteries were in poor condition see #1).
- Is the environment where the UPS is located air conditioned and clean?
- What size motors are being fed?