I was bored yesterday and reading through some old postings when I came across one that was similar to a situation I was examining a couple of weeks ago. My version is just a little more complicated, and since it took a dozen or so replies to answer the first version, I thought I would pose this version.
The original question was if you had a 120/208 wye system (with phase to neutral loads) 10 amps on phase A-N and 10 amps on phase B-N, what is the current in the neutral?
So here is the version that I am looking at, and this does apply to real-world application. The system is based on a 5-wire cable with each set of 120 volt outlets feeding from separate phases...blah, blah, blah.
The original question was if you had a 120/208 wye system (with phase to neutral loads) 10 amps on phase A-N and 10 amps on phase B-N, what is the current in the neutral?
So here is the version that I am looking at, and this does apply to real-world application. The system is based on a 5-wire cable with each set of 120 volt outlets feeding from separate phases...blah, blah, blah.
- On the A-phase outlet, you have a frosty machine which is 20 amps at 120 volts, and an inductive powerfactor of 0.8.
- On the B-phase outlet you have incandescent tent lighting which is 20 amps at 120 volts and a unity powerfactor.
- The C-phase outlet is not being used.
- What is the current in the neutral?
- For extra credit, what is the simplest way to reduce the current in the neutral, and what will that current end up being? (NO! You can't just unplug the loads.)