I admit that I am at a loss.
We are doing a temporary power and have the following situation:
15kw portable gas generator that is rated at 125 amps.
We were looking to hook it up with so cord #2 3 conductor or 1/0 3 conductor Type "w" cable.
Homeowner wants it for temp power in the event of power failure. Originally spec it with a 200 amp double throw switch with pin and sleeve connectors but the price was way too high for him.
Second solution was to backfeed a 100 amp breaker on the panel and use the main breaker interlock kit for the GE panel. Is the #2 SO cord rated for 100 amps or do we have to go with the 1/0.
I've looked in the NEC but again, I'm at a loss.