It would be for service disconnectes rated 1000 amps or more for the ground fault protection, but I really doubt we are talking about generators of that size in this thread.For services 800 amp or more the neutral must be switched due to GFI protection. For smaller systems the only hazard would be the parallel neutral caused by bonding at the gen. and not switching the neutral. If you lost the neutral from the gen. then you would put unwanted current back on the normally non-current carrying parts. As a hazard to linemen there wouldn't be any as the return current on the generator wants to return to its source.
The real world facts are it is not allowed, as you well know, the same as not allowing the same redundant bonding in sub-panels.
As far as the unwanted current on normally non-currrent carrying parts, the code requires us to create that type of situtation for services, so I don't see a real world issue with this application....just a code issue.