Insert a new 702.11(C) as follows:
(C) Classification of Supply. A generator with a grounded circuit conductor connection as part of its output shall be wired as a separately derived source unless its grounded circuit conductor is not bonded to the frame, or where used to supply a premises wiring system it shall be permitted to be wired as a nonseparately derived source if all of the following conditions are met:
(1) The generator rating does not exceed 15 kw.
(2) The generator is connected through a flexible cord and a cord connector to a flanged inlet.
(3) The flexible cord does not exceed 4.5 m (15 feet) in length.
(4) The flanged inlet connection point is not more than 3.0 m (10 feet) from the main bonding jumper or system bonding jumper for the supplied premises.
(5) The point of connection is marked ?Disconnect cord when generator is not in service.?
(6) Ground-fault protection of equipment has not been installed on any portion of the premises wiring system supplied by the generator.
Informational Note: Current product standards require all portable generators rated 15 kw and below and supplying grounded output circuits to have the grounded circuit conductor connections bonded to the generator frame.