I am in agreement with you, this is nothing more than an ungrounded system. If you connect it to a premises wiring system that is grounded it then becomes a grounded system, and technically you should have a separate EGC back to the generator frame to bond the frame.I dont think there is any. It is an ungrounded isolated power source. A fault should not shock you. Two faults maybe, but you or the dirt need to be involved. If the genny case is plastic, that further isolates you from earth making a shock less likely. GFCI is a secondary failsafe.
A negative for bonding it at the factory is that is technically not allowed with a solid neutral transfer switch. Mist people dont have transfer switches that switch the neutral.
Otherwise if there is no ground reference, a ground fault is not a hazard it simply becomes a grounded system, but a second fault can become a hazard.
The problem with electronics is mostly because the small size of the source in comparison to utility sources. Sudden change in load on the small flywheel will either drag voltage and frequency down or allow increase, usually temporary but if the item is sensitive to such fluctuation it will have issues. A 5kW load will have a noticeable effect even on a 25kW portable when the load switches on/off but this kind of load is negligible to effecting volts/frequency to a megawatts range generator the grid is using as primary source.