davidaengelhart
Member
Not sure if this question has been asked already but can the inlet for a portable generator properly connected per 702.5 be located in a garage, or doesn't article 400 apply to the cord?
I think that it depends on how you interpret 400.12(3) if you consider a garage door a doorway.Not sure if this question has been asked already but can the inlet for a portable generator properly connected per 702.5 be located in a garage, or doesn't article 400 apply to the cord?
406.7(B) Connection of Attachment Plugs.I have a 4K portable generator that I plug into an unused 30-amp garage dryer outlet which back-feeds a two-pole 30-amp beaker in the main panel. Works like a charm every time the power goes out ! I do turn off the 125-amp main and I installed an indicator light to let me know when the power is back on.
406.7(B) Connection of Attachment Plugs.
Attachment plugs shall be installed so that their prongs, blades, or pins are not energized unless inserted into an energized receptacle or cord connectors. ...
You also are required to have some type of mechanical interlock and a sign on the service equipment as well as the inlet.Looks like I violated the Section 406.7(B). I have a cord with exposed blades one end connected to the generator and the other to the driver outlet. This is of course just for me. I would never do this for anyone else.
Beside the suicide cord, you're lacking an interlock that makes it physically impossible to interconnect the two sources.I have a 4K portable generator that I plug into an unused 30-amp garage dryer outlet which back-feeds a two-pole 30-amp beaker in the main panel. Works like a charm every time the power goes out ! I do turn off the 125-amp main and I installed an indicator light to let me know when the power is back on.
I think that it depends on how you interpret 400.12(3) if you consider a garage door a doorway.
“It can be installed indoors but we recommend not to.”
The generator must be outside the garage, the inlet is inside of the garage therefore you have to run the cord through the garage doorway. It would need to be specifically permitted by 400.10(A). I guess that one could argue that (3) may apply.How is it any different than a temporary extension cord taking power from a garage receptacle to something out in the driveway?
-Hal
I've seen kits that allow the exhaust to be piped out the wall and generater operate inside the garage. But it makes the generator no longer portable in the the exhaust is modified with perminant piping.
This is a feeder and 250.122 applies.Is #10 ground suitable for the portable generator connection?
I want to re-purpose an unused 6/3 w-#10 ground range circuit by bringing it outside into an inlet like this, and install an interlock kit in the panel I will be feeding. 10KW (12.5KW peak) generator w/ built-in 50A C.B., no doors or windows within 15 feet of proposed inlet.
I have looked all over the NEC and cannot find where the difinitive answer is.
Does 250.122 apply to this?
250.66 seems ridiculous