Power Co.shut down bldg. owner gets 8kw gen.and disconnects feeders to 1phase/3wire 240v. cb panel.Hooks up a spliced cord from gen. to cb panel .Powers up gen.smokes 2 computors and 2 printers.I found that the wired plug was wired 2hots and neutral,no ground,and pluged into the gen,plug of ( 4wire/120v.-240v. ).( the neutral plug prong was properly connected to the neutral slot of the gen.plug ).During operation the spliced cord due to poor splice lost 1 hot leg which resulted in the other leg to jump up to 240v. to neutral, frying the office equip.The gen.plug brkr.did not trip.
Q. Can anyone explain why this happend? and how to prevent this.Is this an inherent gen.design that allows this to happen? or a wiring problem?
Please advise.
Q. Can anyone explain why this happend? and how to prevent this.Is this an inherent gen.design that allows this to happen? or a wiring problem?
Please advise.