2011 NEC (590.6)requires portable generators 15 KW and less to:
1. All 15-20-30 125/250 Volt receptacles to be GFCI protected
2. Those receptacles above must have bubble covers
3. You can use a portable GFCI on a generator mfg or remfg prior to Jan 1, 2011
Please understand that when the generator is used with a MTS, the GFCI will trip due to the main bonding jumper. This will cause problems, and not sure what will happen with homeowners.
Questions
The assumption is generators mfg after Jan 1, 2011 will have GFCI protection. Is this a UL requirement?
Can we enforce the Jan 1, 2011 requirement in an area where the 2011 NEC is not adopted yet?
If the generator is sitting on a truck bed, isolated from earth, and there is a faulty tool, will there be a ground fault path for the GFCI to trip?
I looked at some Honda generators today. The construction generators have GFCI protection for the receptacles.
1. All 15-20-30 125/250 Volt receptacles to be GFCI protected
2. Those receptacles above must have bubble covers
3. You can use a portable GFCI on a generator mfg or remfg prior to Jan 1, 2011
Please understand that when the generator is used with a MTS, the GFCI will trip due to the main bonding jumper. This will cause problems, and not sure what will happen with homeowners.
Questions
The assumption is generators mfg after Jan 1, 2011 will have GFCI protection. Is this a UL requirement?
Can we enforce the Jan 1, 2011 requirement in an area where the 2011 NEC is not adopted yet?
If the generator is sitting on a truck bed, isolated from earth, and there is a faulty tool, will there be a ground fault path for the GFCI to trip?
I looked at some Honda generators today. The construction generators have GFCI protection for the receptacles.