jwelectric
- North Carolina
Anyone remember this?
For feeding a permanent premises panelboard with temporary power when service is not energized? No permanent transfer switch necessary... but if service conductors are installed, I'd effectively isolate and lockout from the temporarily energized portion of the system.Would you also agree that we wouldn't need a transfer switch either?
YesHelp me out just a little bit here.
Should I plug a cord into the 240 volt receptacle on the generator pictured above and connect the cord to a transfer switch that does not switch the grounded neutral conductor the code mandates that the bond to the generator frame be lifted.
Do we agree so far?
I don't see how any issue under 250.34 would change a portable generator to a permanently installed generator. 250.34(A) simply gives the conditions under which a portable generator is not required to be connected to a grounding electrode. It does not say the frame cannot be connected to a grounding electrode.Now should I decide to plug another piece of equipment into one of the 120 volt duplex receptacles on the generator above would that piece of equipment be protected as outlined in 250.34? If you answer this no then the generator can not be a portable generator as described in 250.34
Okay here you go
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions:
(1) The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(2) The normally non–current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
(B) Vehicle-Mounted Generators. The frame of a vehicle shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by a generator located on this vehicle under the following conditions:
(1) The frame of the generator is bonded to the vehicle frame, and
(2) The generator supplies only equipment located on the vehicle or cord-and-plug-connected equipment through receptacles mounted on the vehicle, or both equipment located on the vehicle and cord-and-plug-connected equipment through receptacles mounted on the vehicle or on the generator, and
(3) The normally non–current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
(C) Grounded Conductor Bonding. A system conductor that is required to be grounded by 250.26 shall be connected to the generator frame where the generator is a component of a separately derived system.
FPN: For grounding portable generators supplying fixed wiring systems, see 250.20(D).
Now I will admit that I am not the brightest bulb in the box but for someone to say that a generator is portable when it is part of the premises wiring is OPINION and I will believe that such a generator is not a portable generator until someone shows me code text that says different.
2011 NEC (590.6)requires portable generators 15 KW and less to:
1. All 15-20-30 125/250 Volt receptacles to be GFCI protected
Please understand that when the generator is used with a MTS, the GFCI will trip due to the main bonding jumper.
If connected as a non-SDS, the grounded neutral to frame bond would be lifted. What would cause the GFCI's to trip?But the question hasn't been answered. And to cause more confusion look at 702.10 (A) & (B)
I think to keep the GFCI from triping it would have to be installed as a SDS.
250.34(C) says the frame must be connected to the grounded conductor when an SDS. Since I assume we are talking about a service-supplied [and normally energized] premises system, the conditions of installation you stated makes this portable generator a non-SDS alternate power source. Therefore, 250.20(D) and hence 250.30(A) do not apply. Furthermore, I see nothing in those two sections that say a protable generator falling under their purvue becomes a permanantly installed generator.
That is a 'swing and a miss'.
I can see where you would think that it was a swing and a miss because I don?t believe you have been reading everything, have you?Nothing in what you posted supports the view that a portable generator that has been grounded becomes a 'non-portable' generator.
250.34(A) and (B) states the conditions under which a portable or vehicle-mounted generator is not required to be connected to an electrode. If the conditions are not met, it must be connected to an electrode as defined in 250.52.And here-in lies the problem. First the portable generator is under the rules of 250.34. Here we are told in subsection (C) that the grounded neutral MUST bond to the frame.
When it is not interconnected with other earth grounded systems, it is chassis grounded (a term which the NEC recognizes only by implicit wording, such as in 250.34). When connected to premises wiring, it becomes earth grounded through the EGC.If this generator has devices mounted on the frame then it must be a stand alone system therefore a separately derived ungrounded system.
How would the receptacles be in violation? You remove the frame to neutral bond, not the frame to receptacle ground connections.Should for any reason this generator is connected to the premises wiring of a building then 250.26 mandates that the neutral conductor be connected to earth. Should this generator be connected to a premises wiring system then the bond to the frame must be lifted making everyone of the other receptacles located on this generator in violation. I couldn’t unplug the generator from the transfer switch and move it to a new location and plug in a piece of equipment without reconnecting the frame bond therefore the generator lost is ability to be portable.
The EGC of the cord would carry any fault-to-frame current to the premises MBJ then back to the generator on the neutral.I am sure that you understand that the very second that the neutral bond is lifted from the frame of that generator then every receptacle on that generator no longer has a fault path.
The note refers us specifically to 250.20(D) and it refers us specifically to 250.30(A), not 250.30(B)(2).The informational note in 250.34 (C) refers us to 250.30 and 250.30(B)(2) sends us right back to 250.34
I've read that article in its entirety before. This time I only need look at the figures to see the article contributors do not fully understand SDS grounding. Note in Figures 1 and 2 the captions state the system is SDS... and specifically the gen-set in Fig. 1.http://ecmweb.com/power_quality/electric_groundfault_current_problems/
I am going on the install of gen. in systems with GFI protection on the mains.![]()
And both are references to SDSThe note refers us specifically to 250.20(D) and it refers us specifically to 250.30(A), not 250.30(B)(2).
back this with code textSo if connected as an SDS, 250.30(A) applies. If connected non-SDS, only lifting the frame bond is required.
Also, make sure you read and understand the two FPN's of 250.30(A).
jwelectric said:A portable generator is an ungrounded stand alone system. Once the generator becomes grounded it is no longer an ungrounded stand alone portable generator.
Mike as is always the case you cannot focus on the question asked.
I had said nothing backs your claim that a portable generator once grounded becomes a 'non-portable' generator.
You still have not shown me anything to change that.
Forget about fault paths, forget about all the other 'stuff' and show me a code section that says that a grounded generator cannot be a portable generator.
It is a very simple request. Lets resolve this one issue before moving on to other ones.
Where does the Code say you have to have permission to connect to any system? The Code does not even say you have permission to connect as an SDS to a fixed wiring system... it only implies that you can.And both are references to SDS
Okay then let me look at these sections
The Note in the 2008 book sends me to 250.20(D) which is titled ?Separately Derived Systems? which sends me to 250.30(A) which is titled ?Grounded Systems. A separately derived ac system that is grounded?..
Both are talking about a ?Separately Derived System?
In the 2011 book it sends me straight to 250.30 which is titled ?Separately Derived Systems?
Just what is the code book trying to say here? Is it saying one thing while others are saying that it is alright to do something else?
The only place that I can find it either code cycle that will allow me to connect a generator as a non-separately derived system is in 250.35(B)
Should you find somewhere that would allow me to connect a portable generator as a non-separately system elsewhere in either code cycle please post it for my benefit.
Ooops! My mistake. The two notes referred to are under 250.20(D) in 2008, and I believe (I only have the 2011 ROP Draft as a referemce) they were moved to 250.30 under the opening paragraph [not under subarticle (A)].By the way neither code cycle has two notes under 250.30(A)
250.34(A) says it don't have to be connected to an electrode... which means there is no GEC.I also believe that you are trying to say that the cord used to connect the portable generator that I posted the picture of would require a #8 conductor to carry the fault current. (see Table 250.66)
I think you put a little extra distance on your path... but otherwise, yes, the fault current has to travel on EGC's to wherever the system MBJ/SBJ is located, the back through the neutral feeder's EGC... but it is a path and sufficiently sized to carry the fault if the connection to the fixed wiring system is made through the grounded 3-wire receptacle. I would never consider connecting to a fixed system though one of the 120V receptacles. How about you?If I understand your set-up a fault current on one of the other receptacles located on the generator would have to travel from the point of fault through a receptacle to the frame of the generator back through the fault path to the premises service panel to the neutral back through the receptacle at the building down the grounded conductor through another receptacle to the system before opening the overcurrent device on the portable generator. Yes by-golly I think this is just how UL tested this piece of equipment. Is this really what you mean to say?
Let's correct some errata in the above......
I think you put a little extra distance on your path... but otherwise, yes, the fault current has to travel on EGC's to wherever the system MBJ/SBJ is located, then back through the feeder's neutral... but it is a path, and sufficiently sized to carry the fault if the connection to the fixed wiring system is made through the grounded 3-wire receptacle. I would never consider connecting to a fixed system through one of the 120V receptacles. How about you?
Boy you had my head reeling and rocking there for a second. What is a PG???The only earth grounding requirement is 250.34(C) which requires the frame to be bonded to the [earth] grounded conductor... but ONLY when a component of an SDS. This requirement can be overridden by 250.6(A) when applicable, and falls under the alteration means and conditions of 250.6(B). Thus the PG can be a component of an SDS and required not to bond the frame to the grounded conductor!!!
An example of the above is where an SDS system is powered by a non-service, isolated-primary-secondary-type transformer and the PG, through a transfer switch where the grounded conductor is not switched, and the SBJ is located somewhere other than the PG.
Additionally, since this is a portable generator, it will never be considered part of the building or structure it may serve. With the disconencting means integral to the PG, the connecting cord is considered a feeder... and only an appropriately sized EGC is required to the building or structure's disconnecting means. It is the building or structure which is required to have a GES... and that gets bonded to the feeder EGC.
Well now being that I have no idea what a ?PG? is I can?t argue this point one way or the other.So again, a GEC is not [absolutely] required to be directly connected to the PG.
There is no such thing as an equipment grounding conductor on the supply side of the main bonding jumper.I think you put a little extra distance on your path... but otherwise, yes, the fault current has to travel on EGC's to wherever the system MBJ/SBJ is located, the back through the neutral feeder's EGC... but it is a path and sufficiently sized to carry the fault if the connection to the fixed wiring system is made through the grounded 3-wire receptacle. I would never consider connecting to a fixed system though one of the 120V receptacles. How about you?
PG = portable generatorBoy you had my head reeling and rocking there for a second. What is a PG???
It requires the frame to grounded conductor bonding when part of an SDS. Connected as an SDS, the neutral is required to be earth grounded, which also means the grounding conductor is earth grounded. :roll:Where does 250.34(C) require any connection to earth???????
When it is a component of an SDS having two sources of energy. See the article ceb58 provided a link for in his most recent post.On a self-contained generator where would there be objectionable current? Where does all this come from???
Man you sure do jump around on issues :roll:I sure wish I knew what this PG creature was. If this transformer is a non-utility transformer then it will fall under the requirements of the NEC and will require that the bonding take place either at the source or at the first disconnect. If this is from the outside then the first disconnect will be mandated by Article 225
The fact that there is a disconnecting means integral to the generator and another disconnecting means at the other end of the cord, which is not the final ocpd for loads, makes the cord a feeder.I don?t think that the fact that it is a ?portable? generator makes the conductors supplying the load feeders. I think that because the receptacle on that generator is protected by overcurrent mandates that any and all bonding MUST take place on the generator. Overcurrent on the feeders would allow us to size the equipment grounding conductor by Table 250.122. If there is no overcurrent device on the feeders then the supply side bonding jumping is required to be sized by 250.66
On a service supplied system, yes... to the service-supply side of the MBJ. But when a PG is connected to the same service-supplied system as a non-SDS source, the grounding conductor to (or should I say from?) the PG is an EGC.There is no such thing as an equipment grounding conductor on the supply side of the main bonding jumper.
And just how many 120V systems do you see nowadays?Well if the fixed system was 120 volts I would fly right into plugging it into one of the other devices located on that portable generator.
So that would be at the generator if you are connected to a fixed wiring system via cord-and-plug... and the PG is not part of any building or structure and is outside the building or structure being supplied, right? So drive a couple ground rod and GEC them to the PG.But what I wouldn?t do would be have the system bonding take place at any place other than where the first overcurrent device was located.
...and that is likely the reason for requiring GFCI receptacles, as noted in the the OP...Even with your correction should something be plugged into one of the 120 volt receptacles on the generator and the path you purpose become lost (someone unplugged the cord to the main bonding jumper) then the 120 volt receptacle would be unprotected from fault current. This is a life safety issue.
Well now you sure have found something in you code book that I can?t find in mine. Which year are you using? Just where does it require to be connected to earth in 250.34??It requires the frame to grounded conductor bonding when part of an SDS. Connected as an SDS, the neutral is required to be earth grounded, which also means the grounding conductor is earth grounded.
Unless this portable generator is in the basement I would say that it is outside. If it is outside then any and all wiring to and from would fall under 225. I thought you knew that we were talking about outside PGs.Everything we've discussed falls under the NEC. And I thought we were talking about grounding of a portable generator. How did we get on outside branch circuits and feeders? Oh... on second thought, don't answer that question.
Any conductor that is on the supply of the bonding jumper IS NOT an equipment grounding conductor!!On a service supplied system, yes... to the service-supply side of the MBJ. But when a PG is connected to the same service-supplied system as a non-SDS source, the grounding conductor to (or should I say from?) the PG is an EGC.