tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
2008 NEC section 590.6 will require GFCI protection for generators on job sites.
If the generator is sitting on the bed of a truck, perhaps have a bad cord with exposed hot wire, you touch the hot wire, how likely will it be that the GFCI will trip?
 
tom baker said:
2008 NEC section 590.6 will require GFCI protection for generators on job sites.
If the generator is sitting on the bed of a truck, perhaps have a bad cord with exposed hot wire, you touch the hot wire, how likely will it be that the GFCI will trip?
I may indeed not trip. If there's not at least 5ma of current flowing to trip the GFCI, you're probably not going to get shocked either. You're a bird on a wire at that point.
 
Kinda what I thought.
I was at a IAEI mtg where this change was discussed and it was pointed out the generators with GFCI won't be compatible with home transfer switches with a solid neutral. The CMPs answer was install a TS that switches the neutral!
 