View attachment 11795View attachment 11796View attachment 11797 Can someone enlighten me on what could have caused this arc on the door to this switchgear. This was found at a fire scene this morning. The machine that this switchgear goes to was not suspect to the fire cause but the machine was damaged in the fire. The fuses are not blown. If you zoom in the metal bar over the left fuse is damaged. The switch gear was still on but the main supplying it was off when I arrived. When I tried to move the lever to the off postion it was stuck.
I think it does look like an arc was present, likely for a while. But if you are sure this was not part of the cause of the fire yet the machine it feeds was IN the fire, then another possibility is this (again, a SWAT):
Smoke and ionized gasses came up the conduit from the machine fire, decreasing the dielectric of the air in the switch enclosure or at the very least, coating everything inside with conductive carbon. That allowed the line side of the switch to jump the air gap either phase to phase or phase to ground, striking an arc. The arc then became self-sustaining as long as the current flowed and there was enough ionized gas and/or subsequent vaporized metal to maintain it. Because the arc was on the line side of the switch, the fuses never saw the current, so they never cleared.