Hello All,
I recently ran into a situation with a rooftop unit opening up its feeder circuit breakers. The RTU is fed by a 50A fused disconnect with current limiting fuses, upstream is a 70A "vintage" SQ-D circuit breaker. And all of this is fed by a 175A "newer" style SQ-D CB.
|
175A )
|
|
70A )
|
50A \ fused disconnect
|
RTU
Come to find out the main compressor of the RTU had a locked-rotor which was tripping its internal protection most of the time, the current was up to over 100A before it cut-out. We had mulitple situations before we discovered the problem where the main 175A CB was opening up, ALONG WITH the 70A CB and (1) 50A fuse of the (3) in the disconnect. Is this simply a coordination issue? I guess I would've expected any one of those to open up but not all three.
Thanks for any opinions or hypotheses on this matter.
I recently ran into a situation with a rooftop unit opening up its feeder circuit breakers. The RTU is fed by a 50A fused disconnect with current limiting fuses, upstream is a 70A "vintage" SQ-D circuit breaker. And all of this is fed by a 175A "newer" style SQ-D CB.
|
175A )
|
|
70A )
|
50A \ fused disconnect
|
RTU
Come to find out the main compressor of the RTU had a locked-rotor which was tripping its internal protection most of the time, the current was up to over 100A before it cut-out. We had mulitple situations before we discovered the problem where the main 175A CB was opening up, ALONG WITH the 70A CB and (1) 50A fuse of the (3) in the disconnect. Is this simply a coordination issue? I guess I would've expected any one of those to open up but not all three.