Quoted to run EGC for light poles that did not have them. Pulled all of them but one home-run. There are 2- THHN #12 solid conductor in 1/2 RMC. I was using the ungrounded conductor for a pull string. I could only get it to budge 1'. Then could not pull it back from the other end. Kept trying, tried the grounded conductor and got 2' then same thing stuck, my head never got in.
Its running right under a parking lot, Parking lot looks like it has sunken. Also tones of cuts and patch work on the parking lot. Tried my tracer but does not work that well underground.
Does this sound like a busted pipe. I could just try and thread a nipple to allow me to put a Grounding bushing on the pipe to achieve the EGC but with the conductors to tight and how much tension I physically put on them I think it should be abandoned.
Any ideas on this would be helpful never ran into one that stoped without the head causing it.
Its running right under a parking lot, Parking lot looks like it has sunken. Also tones of cuts and patch work on the parking lot. Tried my tracer but does not work that well underground.
Does this sound like a busted pipe. I could just try and thread a nipple to allow me to put a Grounding bushing on the pipe to achieve the EGC but with the conductors to tight and how much tension I physically put on them I think it should be abandoned.
Any ideas on this would be helpful never ran into one that stoped without the head causing it.