so this is my situation.
Their is a main 400A circuit breaker in a disconnect, mounted on the side of the building. If you come off the 400A breaker into a building with 500kcmil 100ft in length, and terminate into a 2 feed through MLO panels with no main or disconnecting means, and use these panels for your branch circuits. are the 500's considered taps and not code compliant? The wire is protected so I'm thinking their still feeders yet they are not terminating into an overcurrent device. Instead Their terminating into the bus bars and feeding the branch circuits. I feel like I'm overthinking this but it seems fine but i kind of think its not code compliant. i appreciate any input.
THANKS
Their is a main 400A circuit breaker in a disconnect, mounted on the side of the building. If you come off the 400A breaker into a building with 500kcmil 100ft in length, and terminate into a 2 feed through MLO panels with no main or disconnecting means, and use these panels for your branch circuits. are the 500's considered taps and not code compliant? The wire is protected so I'm thinking their still feeders yet they are not terminating into an overcurrent device. Instead Their terminating into the bus bars and feeding the branch circuits. I feel like I'm overthinking this but it seems fine but i kind of think its not code compliant. i appreciate any input.