Possible to extend transfer switch location?

Status
Not open for further replies.

Rig84

Member
Location
Maryland
Occupation
Electrician
So I’m putting in a transfer switch for my parents home, a 50 amp manual switch just to run the essentials during an outage. My dad has a hard time getting up and down the stairs to the basement, think more of a celler basement, low ceiling and uneven floor. My question is would it be ok to “extend” the wires via conduit to the top of the stairs, so he could just open the door and turn the switch from there? Roughly 25’ from panel. Thanks in advance for any help!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
As long as the normal power conductors are on the load side of the service OCPD, they would be feeders and not subject to any length restrictions. If the normal power conductors are service conductors, that would be a violation.
 