Potential failures from poor conductor sizing practices?

Merry Christmas

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I am a fan of 1/0 copper. You get the most ampacity per $ in parallel runs. although sometimes it does not work out as well as other times.
1/0cu x 3 gets 320A within 75C column, relying on software load shedding for future expansion.

Unless 4 wire lugs can be installed for future expansion of one more 1/0 ?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I have only used each once. 750 AL isn't horrible, but it does suck. 750 CU is completely awful. I think I am still sore from the having to wrestle that and that was 6 years ago 🤣
When I was working as a full time commercial PV system designer, out installation guys asked that I not specify conductors larger than 500kcmil. When I needed more ampacity I went to multiple sets. One reason for that is that most of the time we were adding to systems where we had to work around existing conductors and conduit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
When I was working as a full time commercial PV system designer, out installation guys asked that I not specify conductors larger than 500kcmil. When I needed more ampacity I went to multiple sets. One reason for that is that most of the time we were adding to systems where we had to work around existing conductors and conduit.
With existing equipment more sets isn't always the answer. For example if your existing 400 amp circuit breaker has only a single terminal for each phase running mulitple set just makes everything more complicated.
 
With existing equipment more sets isn't always the answer. For example if your existing 400 amp circuit breaker has only a single terminal for each phase running mulitple set just makes everything more complicated.
I find equipment lugs to generally be lacking in number of ports. 400A with one terminal is really lame. Like even 1200A stuff usually only has 4 ports. Maybe I am an unusual case because I work alone 99% of the time I tend to go for a more sets and aluminum.
 

MCosentino87

Member
Location
New York
Occupation
Electrical Designer
When I was working as a full time commercial PV system designer, out installation guys asked that I not specify conductors larger than 500kcmil. When I needed more ampacity I went to multiple sets. One reason for that is that most of the time we were adding to systems where we had to work around existing conductors and conduit.
The company I work for doesn't usually go over 600kcmil because of diminishing returns (you'll notice the curve flatten around 600 in ampacity tables) and ease of installation for the contractor.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
With existing equipment more sets isn't always the answer. For example if your existing 400 amp circuit breaker has only a single terminal for each phase running mulitple set just makes everything more complicated.
Be that as it may, I set 500kcmil as the largest conductor as the default; if they wanted something different they told me.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Be that as it may, I set 500kcmil as the largest conductor as the default; if they wanted something different they told me.
For us 750 kcmil is the largest size we would ever use. And for something like a 400 amp feeder never parallel #3/0's, one set of 600 kcmil. Maybe it's a regional thing but we almost never see parallel condcutors smaller than 250 kcmil.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
For us 750 kcmil is the largest size we would ever use. And for something like a 400 amp feeder never parallel #3/0's, one set of 600 kcmil. Maybe it's a regional thing but we almost never see parallel condcutors smaller than 250 kcmil.
I only design stuff with parallel 1/0 copper but they are only inside of enclosures so the cost is not as big of a deal. I don't like having a bunch of unused scraps of wire laying around and if I always try to use 1/0 the leftovers will get used up on the next project.

Last time I looked, we had left over wire out in the shop that we bought several decades ago and have not managed to use yet.

Once I suggested we just use what we have laying around even if it was bigger than needed. My suggestion was declined on the grounds that it would add cost. I don't know how it adds cost to just use something you already paid for.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I don't know how it adds cost to just use something you already paid for.
Bean counter mentality right there... I've run into that many times in my career, I still don't get it. I was told once "Well it's the cost of replacement that counts!". But if you have been sitting on it for 5+ years and not had an occasion to NEED it, why on earth would you replace it? In fact, as I kept getting repeatedly told, old inventory was "written off" after some length of time, so from an owned cost perspective, the value is zero and if you don't need to replace it, then why would you care? But that's why I hated accounting...
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
For us 750 kcmil is the largest size we would ever use. And for something like a 400 amp feeder never parallel #3/0's, one set of 600 kcmil. Maybe it's a regional thing but we almost never see parallel condcutors smaller than 250 kcmil.
When I was an estimator for a medium size shop, the owner and I did a bunch of cost analysis and smaller parallel conductors always won out on cost. We would never work with anything over 500, maybe 600, but on services only.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
When I was an estimator for a medium size shop, the owner and I did a bunch of cost analysis and smaller parallel conductors always won out on cost. We would never work with anything over 500, maybe 600, but on services only.

Out of curiosity, did this include cost of conduit? Like EMT or RMC or something with the parallel conductors? Was this 3 wires or 4 wires per circuit (3ph with neutral or no neutral)?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Out of curiosity, did this include cost of conduit? Like EMT or RMC or something with the parallel conductors? Was this 3 wires or 4 wires per circuit (3ph with neutral or no neutral)?
The thing is two smaller wires in parallel with the same ampacity as a larger single conductor will generally fit in the same size conduit and even derated from the 90 degree column for six ccc in the conduit you still typically come out ahead.
 
When I was an estimator for a medium size shop, the owner and I did a bunch of cost analysis and smaller parallel conductors always won out on cost. We would never work with anything over 500, maybe 600, but on services only.
I would be skeptical on the "always" part. Although I generally prefer more smaller parallel sets, seems like they're just too many variables to say it's always going to be more cost effective.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I would be skeptical on the "always" part. Although I generally prefer more smaller parallel sets, seems like they're just too many variables to say it's always going to be more cost effective.
You can probably come up with some odd ball case where it isn't. But I bet you cannot come up with a case where aluminum is not cheaper than the same ampacity of copper, where aluminum is an option.
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
I would be skeptical on the "always" part. Although I generally prefer more smaller parallel sets, seems like they're just too many variables to say it's always going to be more cost effective.
There may have been some (very few) occasions that it didn't win out, but it was definitely more cost affective for multiple smaller wires most of the time.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Smaller sets may be more economical in many scenarios but I think that would apply more when you had lower labor costs. More conductors equals more pulling, possibly more raceways, more terminations, and more man hours.
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
Smaller sets may be more economical in many scenarios but I think that would apply more when you had lower labor costs. More conductors equals more pulling, possibly more raceways, more terminations, and more man hours.
Thats true, but the smaller everything is the quicker the work can be done. And the materials are less expensive even if you have to buy more. At least thats what I remember. Its been a long time since than. Things may be different now. For the life of me, I don't know how nay of you guys price anything these days the way the price fluctuates every hr on the hr it seems.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Smaller sets may be more economical in many scenarios but I think that would apply more when you had lower labor costs. More conductors equals more pulling, possibly more raceways, more terminations, and more man hours.
Why more conductors equal more pulling or more conduits? There will generally be less copper so the parallel conductors should fit in the same size conduit.

As for extra labor for terminating, I can't imagine that terminating one large wire is much difference time wise than two smaller ones.


But, if you set your mind to it, you might be able to come up with an odd ball case where it is cheaper to run one wire where you could run two parallel ones instead. I think it is mostly a mindset like how electricians wrongly believe copper is somehow better than aluminum and thus waste who knows how much money on copper when aluminum would be far more cost effective and just as safe.
 