Re: Pottery Kilns tripping breakers
The kilns that I have looked at come with an 8' Cord and Plug. The cord has " 2 - 6 / 1 - 8 / SRDT " printed on it.
I do not know what SRDT means, just guessing the S is Silicone and the R is Rubber. Have made many-many cone 8 firings over the past 30 years and have not had a problem with the supply feeder, the receptacle or the factory cord and plug.
Have changed many-many elements and factory installed "on - off" switches which are for each set of elements.
I am talking of "HOBBY" class kilns.
Depending on the kiln size, they usually range from one element to six elements in the kiln.
Thus, it is very easy to get elements which are not designed for "THAT" kiln.
If you know the voltage used, the number of elements and the total wattage (which is on the Name Plate ), the kiln manufacturer will tell you what elements to use.
The element comes a specific length with the terminal ends folded back to make( I suspect ) more contact surface at the termination point.
Again, without knowing the actual installation details, the ambient temperature could be a problem on any long term firings.
Knowing the following for EACH kiln would help in making a judgement:
Name Plate Data; Volts, Amperage, Wattage.
Actual voltage reading(s) of the supply, both at the OCPD and at the Kiln terminals. (or at least at the receptacle).
Acutal Amperage reading(s).
Acutal 'field installed' wiring sizes.
If using a Kiln-Sitter, the typical "cone" being used when the trouble appears.
Did not mention before, but the earlier method was to set three cones on a stand in front of a "port hole" to observe the cones occasionally.
One cone was of a less heat rating and one cone the desired heat rating and a third cone above the desired heat rating.
When observing the sagging of the "less" heat rating, you knew to check very often to see when the desired heat rating cone strated to sag and then "turn OFF the kiln". The third, higher rated cone was to check if an "Over Firing" occurred.