My issues is with the cord, at no time have I said I have an issue with the two boxes, NM cable, and two devices.
iwire,
I respect your posts and thinking this through with us.
May I better understand what specific issue you see with a UL/CSA Listed and rated power supply cord? We are not making these in a back-room with non-compliant copper wire and plastic jackets, trust me.
Supply cords are what are used on all appliances.
With reference to NEC 406.6 (D): An INLET can only be energized from a power supply cord. If you accept the INLET as an NEC and UL recognized device, then the logic of a power supply cord would need to be accepted too.
I sense from previous posts, your real issue is the PowerBridge being used to energize an entire premise circuit or a room circuit with multiple outlets with a simple power supply extension cord. Its just not possible.
This is not the intended use or the capability of a PowerBridge. The power supply cord-set has a maximum wattage rating of 1850.
No one has contacted PowerBridge with the question to use it as a house premise wiring method. We have never suggested or heard of anyone using a PowerBridge in this manor.
The marketing is specific to
extending power from point A to B not more than that, with the benefit of connection to an external power surge conditioning UPS device.
Which if you think about it, they are energized by a power supply cord plugged into the front of the circuit.
Installing a PowerBridge accomplishes the same, EXCEPT using Code compliant building wire/cable (NM/MC) inside the wall to extend power up to the appliance (TV)
NOT to power a dwelling, it's simply not rated to accomplish that concept and would not be approved by any AHJ understandably due to the rated capacity of the cord set, so you are correct not be acceptable with that possibility.
Is this being over-thought in the basic concept? This is not a branch circuit, infact it can be argued it's not a circuit at all. Its DEAD until energized from a plugged in power supply cord. This is an
extension not a circuit, using NM/MC wire in the wall to extend the EXISTING circuit power from the front-end as intended, not branch wired from the backside as part of the permanent premise wiring circuit.
PowerBridge is a simple solution to a recently new problem. High-level power protection to an expensive display device from external protection. There is no other way to accomplish this that we are aware of.
Regards,
Justin
PowerBridge