141123-1414 EST
StephenSDH:
It is not that I don't know how to calculate the total power, it is a lot of work, but rather I think you may have a faulty system design. Now that you have introduced the fact that there are 32 zones with individual controllers, and you only want to monitor three line currents, then I believe you have major problems for total power measurement to detect a single heater failure. Power measurement is not needed to detect a heater failure. This comment is modified by my rereading your first post. See below.
If all you want is total power, then the Load Controls device will directly provide this information with one signal for your total system. This automatically uses all three currents and three voltages to calculate total power. Because of the design of the power monitor there is compensation for differences in the three phase voltages.
I do not have good information on accuracy and repeatability, but it is listed as 2.5% of full scale for accuracy, and 0.25% for repeatability. Minimum response time is 15 milliseconds (one full 60 Hz cycle). Nothing on zero drift or temperature coefficient.
Your present approach of measuring current is going to produce some time varying ripple resulting from the random operation of the various contactors.
Going back and rereading your original post I see you mention individually switching the zones to measure one zone at a time, and that there were several heaters per zone. Several meaning not very many, apparently about three. Thus, to sense that a heater element has failed will show up as a change in two of the three currents. The change will be at least moderate because of only a few heating elements. Easy to detect. Now from later posts we know individual zones have individual controllers and contactors.
winnie is apparently sending you a spreadsheet with the solutions to the simultaneous equations. He has done all the work for the simultaneous equations solution.
.