Free Electron
- Upstate New York
I need some ammo.
My company installed a 200 amp, 120/208v, 3 phase M.L.O. panel in a store 150 feet from the main switch board. The switch board is ( if I remember correctly) 1600 amps, 120/208 with a main disconnect, with 8 to 10 cold sequence meter compartments that all have lockable ocp device breakers before the meters. The meter installer would not install the meter for this store, claiming the MLO panel we installed needed a main breaker. I explained to him the load center is already protected by the switchboard breaker and it was inspected and approved by an electrical inspection agency. This is where he called his supervisor for direction and was told it was in the code and we will needed a main breaker. I asked please state the article in the NEC ,which he couldn't. He is hung up on the breaker being installed before the meter and nothing after the mater. When he looked at some of the other existing stores they had main breakers in them. Needless to say he left without installing the meter, leaving my customer looking at me for a solution. Anybody ever run into this??