Power Distribution Block in NEMA4 box in a Class 1 Div 2 Location

Status
Not open for further replies.
Your link has a problem.

If otherwise used within their intended design applcation, there is no additional prohibition with created by use in Class I, Division 2.
 
Here is some information about the PDB. It is a UL recognized device. As i mentioned before, i plan to install it inside a NEMA4 enclosure in a class 1 Div 2. I just want to make sure it is OK to do so. Thanks
 

Attachments

  • 1492pd31123.jpg
    1492pd31123.jpg
    65.3 KB · Views: 1
Here's your problem. That is a UL "Recognized Component" (the backwards "UR"). That means it is intended to be used in specific equipment and has no "general" application. Class I, Division 2 has no bearing, but it is possibly a misapplication as you have described it.
 