chris kennedy said:110.14?........
On a piece of equipment with 2 or more electrical cabinet's. Feeders from the service disconnect to a power dist. blk. on line side. Load side of dist. blk.connects to other load centers & circuit breakers. Basicly using the power dist. blk's as a busway. Would article 368 be used to determine conductor size and length?bphgravity said:Do have a more specific question ???
The load side conductors are tap conductors and 240.21(B) applies.Busway. A grounded metal enclosure containing factory-mounted, bare or insulated conductors, which are usually copper or aluminum bars, rods, or tubes.