Re: Power draw on 208V single phase ckt served by 208/120V t
I just made the following comment on that ?other thread.? But for completeness, I will repeat it here.Originally posted by rattus: Consumed by the load, 2080VA, but the xfrmr thinks it is delivering 120x10x2, or 2400VA. If you are concerned about the xfrmr load, I would go with 2400VA. Whole nuther thread on this subject.
The correct total load is 2080 VA, not 2400.Originally posted by charlie b: The transformer thinks it is delivering 1 x 120 x I VA plus another 1 x 120 x I VA. But these two do not add up to 2 x 120 x I VA. Rather, they add up to 208 x I VA.