No mention of PFC other than yours. We need confirmation PFC is involved and the actual data to proceed down that path.My second guess is OP's load is overcompensated and has leading load power factor. His transformer's inductance compensates leading load power factor and improves line side power factor.
What? Do you mean to imply that a utility might try to manipulate their revenue stream by carefully planning where they place their meters? Unheard of!
:lol:
There is no PFC in the substation. And the load is mostly inductive, it's a large industrial plant (40 MVA total, with about 27 coming from on-site generation, so we're buying around 13 MVA).
If the transformer is a delta primary, wye secondary, could it be the phase transformation that's causing this? These types of transformers have a 30 degree phase change correct?
The POCO power factor metering is on load side. Right? If so, it is only to be ascertained whether they are recording a leading power factor. If yes, it answers your OP query. If no, it is likely defective metering.There is no PFC in the substation. And the load is mostly inductive, it's a large industrial plant (40 MVA total, with about 27 coming from on-site generation, so we're buying around 13 MVA).