HYPOTTHETICAL question. If I hade a motor that hade 50% power factor and the amps draw was 3 amps @ 120 v and watts were 185 would the voltage drop on the wire be the same as a motor with about 100% power factor that pulled 3 amps and 350 watts ?
 

MD84

Senior Member
Location
Stow, Ohio, USA
Good question. I do not have an exact answer for you. I will venture a guess and say that the voltage drop will be less on the lower power factor circuit. This is because the voltage and current are not in phase.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
160308-0822 EST

If you measure the voltage across the section of wire with the 3 A of current flow in it, then the drop along that wire is the same independent of the load power factor.

However, if you define voltage drop as the change in voltage at the load point from no load to loaded, then when the load is not unity power factor you need to do a vector calculation to determine voltage drop.

For small voltage drops it does not make much difference.

.
 
Last edited:

dkidd

Senior Member
Location
here
Occupation
PE
There is a very small difference due to power factor. It is the small vector labeled error on the attached.
 