- Illinois
- retired electrician
The following was in an e-mail newsletter that I get. I don't think the last sentence is correct. It is my understanding the the only savings by putting the power factor correction at the load it the reduction in the I^2R losses on the feeder conductors. Would that amount to "far more kW per hour"?
Why are we talking about PF at the feeder level? If you correct it at the entrance, then you avoid the PF penalties from the electric utility. But that?s all you do.
You may have PF of 99% at the service and only 77% at the load. This means the load has to draw significantly more power to do the same amount of work. You aren?t paying the higher rate per kWH, but you?re using far more kW each hour.