I assume you are saying motor is only loaded to around 58% of it's rating, current wise.Hi, The PFCC will be connected as attached image, however, the motor line has current of 58% of the motor FLA.
So, when calculating the capacitor VAR, should I multiply 58%?
---> (VAR=58% x KW x multiplier Kk from table)
Thanks a lot.
I think his ? is does he size the cap for the Y starting i (FLA/sqrt 3 or 0.577 x FLA) or for the delta running 100% FLA
???
I would size for FLA and check against starting amps (keep pf <0.95 lag)
adjust kvar within those limits
Although corrected pf should be similar at both points
starting kva is lower but so is pf
running kva will be larger but with improved pf
so correction (kvar delta) for a given kvar should be similar at both points
may sketch it out later
I think the 58% comes from 1/sqrt(3), the ratio of the wye to delta voltage.I assume you are saying motor is only loaded to around 58% of it's rating, current wise.
I think the 58% comes from 1/sqrt(3), the ratio of the wye to delta voltage.
Based on my experience, the motor reactive component doesn't change much with load. That's why a single, fixed value PFCC is usually what gets fitted.
I agree.The brief wye start can be pretty much disregarded in my opinion.OK, so with a wye start delta run, is it worth while to even consider what the power factor may be during the very brief wye start period, especially if power factor averaged over a longer time period is what you pay penalties for and is only reason you are correcting PF in the first place?
I agree with that. We always fitted a contactor for the PFC.The purpose of PFC caps is to correct the power factor of the motor when running. It does not matter where they are in the circuit as long as they are in parallel to the motor. They are sized to raise the PF to .95 or better by adding VARs to compensate for the inductive properties of the motor. Using the .58 value of the contactor in the sizing of the caps simply results in the caps being under sized by 42%. Might as well not bother putting them in at all because if the capacitance is insufficient to raise the PF to .95 or better, you will still suffer the penalty from the utility.
Given the potentially dangerous torque spikes that can result in using Y-Delta starting, I would never arrange for caps to be on line until after it has transitioned to Delta. For that reason, I always add a 4th contactor feeding the caps, controlled by the aux contacts so that the caps do not come on line until the Wye contactor opens. So you put a NC aux from the Wye contactor in series with a NO six from the main contactor.
The purpose of PFC caps is to correct the power factor of the motor when running. It does not matter where they are in the circuit as long as they are in parallel to the motor. They are sized to raise the PF to .95 or better by adding VARs to compensate for the inductive properties of the motor. Using the .58 value of the contactor in the sizing of the caps simply results in the caps being under sized by 42%. Might as well not bother putting them in at all because if the capacitance is insufficient to raise the PF to .95 or better, you will still suffer the penalty from the utility.
Given the potentially dangerous torque spikes that can result in using Y-Delta starting, I would never arrange for caps to be on line until after it has transitioned to Delta. For that reason, I always add a 4th contactor feeding the caps, controlled by the aux contacts so that the caps do not come on line until the Wye contactor opens. So you put a NC aux from the Wye contactor in series with a NO six from the main contactor.
Thanks a lot for the answer.
I sized the capacitor simply based on the motor KW. 58% was not in the calculation.
C=VAR/(6*pi*f*V2), and in delta connection, Vp=VL --> current is irrelevant, size of the capacitor that delivers the needed VAR will not change in this case whether being put on the main line, or the delta.
How did you arrive at the VAr and why 6 rather than 2?
what C (or VAr) did you arrive at?
6 for 3phase.
VAR I get is the total of 3 capacitors, C is for each capacitor.
To solve for C using your equation you must know the VAr
how did you determine that value?
what is it? 50, 100, etc ???
what is?
voltage
HP
FLA
non-corrected or motor pf
???
Um......check the diagram provided by the OP.FanYu...
Are your Caps configured in Delta or Wye?
Regards, Phil Corso
FanYu...
Are your Caps configured in Delta or Wye?