Power factor correction capacitor sizing for a wye-delta motor connection
FanYu...
It has to do with a phenomenon referred to as "self-excitation of a motor upon disconnection from its power supply"! The subject was covered extensively in a Post titled "OverCorrection"!
FanYu...
"Delta is usually preferred, because you get only 1/3 total VAr from a Wye."
Correct, but for a different reason! The delta-connection is less likely to become a problem if source of supply is single-phased!
Do you know the equation to determine capacitance or kVAr... w/o a chart?
Phil
In 3 phase, the 3 capacitors are either connected in wye or delta.
Delta is usually preferred, because you get only 1/3 total VAR from a wye.
You'd use cifferent value capacitors with a different voltage rating in star. Not something I've seen done very often............
FanYu...
Phil
Good to know that.
Yes
VAR= P * ( tanφ1 - tanφ2)
Actually, it does.
You must be getting a different drawing then I am then. All I see is a box with three leads that end at the outline of the box and the box is PFCC and has a single capacitor symbol inside the box as well - no other details of how individual capacitors within that box may be connected.
That said isn't the net KVAR of the unit mostly all we care about?
You must be getting a different drawing then I am then. All I see is a box with three leads that end at the outline of the box and the box is PFCC and has a single capacitor symbol inside the box as well - no other details of how individual capacitors within that box may be connected. That said isn't the net KVAR of the unit mostly all we care about?
kWired...
Right on: a) Dwg observation, b) conclusion!
Phil