I am sorry you misunderstood it:Maintaining the required slip means maintaining the required speed.
No misunderstanding on my part.
Did you miss this:
Minimum input power and maximum efficiency occur at a characteristic
optimum slip value
Now, what do you think optimum slip value is?
Look back at #177.
Do you
really think optimum slip is 0.3 pu?
I think the paper is about voltage optimisation,
not speed control.
It's a feature that some variable frequency inverters have typically for cube law loads like fans and pumps. The V/f ratio gets reduced for lower speeds but it's for energy savings, not a method of speed control. I'm not sure how effective it is for energy saving. Reducing the voltage reduces stator current in the stable region and that may reduce stator losses some. It also increases the slip a
little. That in turn increases rotor current. Which increases rotor losses and the increased current reflects back to the stator side. In short, each case needs to be looked on its merits. I have tried it on some fairly big VSDs with no convincing figures to demonstrate any savings.
That said, I do believe that voltage optimisation for fixed frequency applications can achieve energy savings. Your #151 example demonstrates that. It also clearly demonstrates that a large change in voltage does not equate to a significant speed difference. And, so far, I think that's
only actual example you have presented.