william talbot
- Livonia, Michigan.
Most utilities impose power factor penalties on customers when exceeding the utility limitations. In our area P.F. below .85
is the point at which the utility imposes the penalty. We install a lot of capacitors which are sized to raise the P.F. above
.85, generally to about .89 keep the cost reasonable.
However, we see more and more loads that create harmonic distortion in addition to low P.F. which affect the operation of
capacitors this problem must be solved by tuning with filters at additional expense. And harmonics are becoming a problem with neutrals being overloaded too; the 'bandaid' solution that the code suggests is to double the size of the neutrals!
I think it is time that the NEC address these problems more seriously. Building owners or tenants should be able to buy
electrical equipment that do not create P.F. nor harmonic effects on utility bills. This would require manufacturers to add
capacitors and if necessary tuned capacitors to avoid customer penalties or, as stated above, increase neutral sizing. Or at
least make it a rule that the enhancement be a manufacturer option for the buyer to choose to pay for.
Years ago the NEC required manufacturers of enclosed incandescent down-lights to install non- resettable thermal cut-outs in their luminaires to prevent overheating. That solved the problem of people using higher wattage lamps to increase
lighting levels which must have resulted in fires in some cases. I see this as an example for the P.F. and harmonic problems which are growing daily; as I see it, like a disease in our industry.