I have been doing a billing analysis for a facility. I am seeing huge variation in Kvar at a facility that gives me unreliable power factor values. I have not been on site so I am not familiar with their loads.
One month I see 16,320 kwh, 8,280 Kvar, and demand of 88.8 kW. That gives a power factor of 93% which is believable.
Two months later I see 33,360 kWh, 19,680 kvar, and a demand of 78.72 kW. That gives me a power factor of 250%.
Other than the sizing of a capacitor bank, what else should we be looking for?