And to further muddy the waters- the relations of excitation, shaft speed, and power output of a generator differ whether it's operated on- or off-grid. On-grid the shaft speed can't vary, and IIRC, you control the real and reactive power by varying the throttle and excitation. When off-grid, the throttle controls both the frequency and real power but the excitation controls the voltage. (Unless I have that backwards, it's been a while.)
I recall some discussion here about this a couple of years ago, but I'm too lazy at the moment to find that.
There are some also nice slides at http://www.drhenrylouie.com/uploads/34-Synchronous_Generator_Operation.pdf and a description of governors for hydro generators at https://www.usbr.gov/power/data/fist/fist2_3/vol2-3.pdf.
But I digress D:
I recall some discussion here about this a couple of years ago, but I'm too lazy at the moment to find that.
There are some also nice slides at http://www.drhenrylouie.com/uploads/34-Synchronous_Generator_Operation.pdf and a description of governors for hydro generators at https://www.usbr.gov/power/data/fist/fist2_3/vol2-3.pdf.