John Altenburg
Has anyone been requested to improve a clients Power Factor to help them get a better utility rate?
What was the outcome and how big was their operation?Yes...............
If you are on the load side of the service point, how would the serving electric utility have anything to say about the customer correcting his power factor?We did a small factory and used an engineer to design the capacitors the POCO wanted a PE seal on the drawings before they would do anything
Offering to reduce or drop the low-PF penalty is a big incentive. They can't demand it, but they can make it an attractive option.If you are on the load side of the service point, how would the serving electric utility have anything to say about the customer correcting his power factor?![]()
Improving your power factor will automatically drop the penalty (eventually) without the utility having to make any special offers. There may be a wait until the load history rolls out of the rate tables.Offering to reduce or drop the low-PF penalty is a big incentive. They can't demand it, but they can make it an attractive option.
As far as I know, most electric utilities have a PF penalty. If the customer doesn't have 100% PF, the serving electric utility must correct the PF in order to keep the substation transformers at a reasonable size, keep their primary distribution lines from being overloaded, etc. They also have to serve kVA, not kW.. . . Not sure there was any benefit to the end user as the local utility had no PF penalty.
If you look closely at the bill, you will find an adder for poor PF OR a credit for PF better than XX% OR everything on the bill in kW and then the numbers change to kVA and a charge for the kVA used (kVA can be reduced with PF correction).
Even without the PF penalty, with correction installed at the load, you will reduce heat losses, lower the voltage drop, and reduce supply equipment size needs. As you know, correction at the meter does nothing for you if there is no PF penalty.Several different projects, on some a single PF correction was installed at the main service.
On others point of use was installed.
In all cases the customers had little or no idea it was part of the design. With the PF off the measured PF with the site up and running was between .82 to .92. Not sure there was any benefit to the end user as the local utility had no PF penalty.
Agreed, unless they were willing to forgive past sins and associated charges and/or demand levels.I just don't understand how the serving electric utility can require anything in the way of a PE stamp.![]()
While I did not review all the bills the ones in Maryland I have seen and saw no penalty noted I looked fairly close.
I remember we used to call the power company when we pegged a meter when we would cut stuff back on after working.around here, on a poly phase service of 400A. or larger, there is a demand
meter with a captive needle that the meter reader resets every time he
reads the thing... the unit price on the KW is based on the demand meter.
high motor starting loads will peg that meter, and that means a higher rate
paid for all electricity used that month.
in the late 70's and early 80's, all grocery stores had interlocked compressors,
so they couldn't start more than one refer compressor at a time.... if the
tumblers lined up, and a bunch of them hit at once, and pegged the demand
meter, the cost of electricity for that 50,000 sq ft supermarket would be $5,000
higher for that month, and that was in the late 70's.
. . . If you look closely at the bill, . . OR a credit for PF better than XX% . . .
I am assuming that you are talking about larger services that have demand and reactive meters. The smaller commercial services are normally treated the same as residential services with respect to PF.. . . and saw no penalty noted I looked fairly close.
Now, it has been our experience working in many large office buildings that those buildings having "power factor correction capacitor banks" installed at the end of each bus duct riser and they are turned "OFF" ???? Some that we checked had blown fuses??? From what we see there is a place for them, but very limited to large factory type areas???