Power for Garage 4 Post Lift

Status
Not open for further replies.

Shorts 53

Member
Location
N. California
Was hoping for some advice on what wire size I should use for a 4 post car lift. The motor is rated at 220v/60hz/1ph with a recommended breaker size of 30 amps. The distance from the electrical panel to the lift motor is plus or minus 100 feet. Thanks in advance for any help.
 

Shorts 53

Member
Location
N. California
Thank you!
I just wanted to confirm what I was reading in Table 310.16.
I will be doing the grunt work (string the wire thru attic space) and let an electrician make the connection at the panel and lift motor.
 