Put your tongue back in and tell me why you think so.
Because I read the thread title and the opening post. :thumbsup:
Put your tongue back in and tell me why you think so.
Because I read the thread title and the opening post. :thumbsup:
IMO, yes the enclosure can be used as a path for equipment ground. Mostly just because common sense would allow it, but that really has no code support. Your next options are stack all the lugs under one bolt or put in an EG bar. I personally put in XXX ground bars because that is what we stock. Don't care whose 40 year old enclosure it is.
That tells us that the metal non-current carrying parts of the service equipment have to be bonded. That does no tell us that the metal parts of the service equipment are EGCs,250.80 (2011).
Sorry I don't have a 2011 NEC avaible but check out NEC 2002, Art. 250.96
Art 250.96 Bonding Other Enclosures.
(A) General. Metal,cable trays,cable Armor,cable sheat,enclosures,frames,fittings and other metal non-current -carrying parts that are to serve as grounding conductors,with or without the use of supplementary equipment grounding conductors.
Ronald )
You left out a key word in your description of what 250.118(13) says.In my opinion 250.118(13) allows it because it says electrically continous raceways. Those who say that the panel is not a reaceway might want to think about the restriction of running branch circuits and service conductors in the same raceway. I once removed the guts of a panel and did the branch circuit splicing in the old panel. I then put 2 nipples out to the new panel and spliced the service conductors in the old panel and ran those thru on nipple and the branch circuits in the other nipple. Guess what? The panel like magic became a raceway!!! red tag city. Everyone on here in a very sprited post all agreed that the panel was a raceway. now we are saying its not?
Other listed electrically continuous metal raceways and listed auxiliary gutters.
In my opinion 250.118(13) allows it because it says electrically continous raceways. Those who say that the panel is not a reaceway might want to think about the restriction of running branch circuits and service conductors in the same raceway. I once removed the guts of a panel and did the branch circuit splicing in the old panel. I then put 2 nipples out to the new panel and spliced the service conductors in the old panel and ran those thru on nipple and the branch circuits in the other nipple. Guess what? The panel like magic became a raceway!!! red tag city. Everyone on here in a very sprited post all agreed that the panel was a raceway. now we are saying its not?