The NEC gives a %tolerance that each phase can be out by. I'm quite sure that it's 10% OR LESS?? Given that, how do you determine the KVA on each phase.
208v * 40a = 8.32KVA. 40amp breaker 2pole is required.
I'm designing a power panel. In it I am showing that each phase of the system is balanced. To do that, the watts or kva on each phase have to be known in order to this. I really know no other way of referring to the amount of Power that can be measured on a Phase. If you can measure the voltage on a phase and measure the current on a phase, then in essence, you have the power being generated, consumed, and transmitted across any given phase.
How else can you show a balanced (phase to phase) system when using 2pole circuits?
[ April 02, 2003, 02:16 PM: Message edited by: jobrafo ]
208v * 40a = 8.32KVA. 40amp breaker 2pole is required.
I'm designing a power panel. In it I am showing that each phase of the system is balanced. To do that, the watts or kva on each phase have to be known in order to this. I really know no other way of referring to the amount of Power that can be measured on a Phase. If you can measure the voltage on a phase and measure the current on a phase, then in essence, you have the power being generated, consumed, and transmitted across any given phase.
How else can you show a balanced (phase to phase) system when using 2pole circuits?